One more valuable link:
Although the subject of this thread was was voltage separation in the
z-axis of a PCB,
I did find a very useful ONLINE CALCULATOR for Creepage and Clearance per
IEC/UL

http://www.creepage.com/

It saves having to wade through the specifications and combine various
tables.
HINT: If you are calculating for a PCB construction, select the "IIIa/IIIb"
Material Group

simple.
(big thanks to Dave Larusso!)

onward thru the fog,
Jack


On Fri, Jun 20, 2014 at 11:47 AM, Karl Bates <[log in to unmask]> wrote:

> This web page is helpful.http://www.smps.us/pcbtracespacing.html
> Karl
>
>
> > Date: Fri, 20 Jun 2014 16:20:52 +0000
> > From: [log in to unmask]
> > Subject: Re: [DC] z-axis separation for high voltage
> > To: [log in to unmask]
> >
> > Jack -
> >
> > There are two different principles at work here. The Table in 2221 is
> for creepage across the surface or along the boundary between layers. The
> bulk insulation given in the slash sheet is perpendicular to the copper
> foil.  You can search on HV creepage and find plenty of information. UL was
> a great resource at one time but I no longer have access to their specs so
> I don't know what they have available.
> >
> > Is the 1700V DC or AC? If AC make sure it is a peak-to-peak voltage, not
> RMS voltage the difference can kill the design.
> >
> > I would recommend that your minimum core is at least 0.13mm with 2
> layers of 1080 glass. And, if it were my design I would probably want more
> like  4 layers of glass and a minimum post processing thickness of 0.20mm
> >
> >
> > Jeffrey McGlaughlin, C.I.D.
> > Engineering Designer
> > Avionics Systems & Tech Refersh
> > Office: 614.424.7582| Fax: 614.458.7582
> > [log in to unmask]
> >
> > Battelle
> > 505 King Avenue
> > Columbus Ohio 43201-2693
> > http://www.battelle.org
> >
> > Connect with Battelle
> > Facebook | LinkedIn
> > Twitter | YouTube
> >
> > This message is intended only for the use of the individual or entity to
> which it is addressed, and may contain information that is privileged,
> confidential and/or otherwise exempt from disclosure under applicable law.
> If the reader of this message is not the intended recipient or the employee
> or agent responsible for delivering the message to the intended recipient,
> any disclosure, dissemination, distribution, copying or other use of this
> communication or its substance is prohibited. If you have received this
> communication in error, please return to the sender and delete from your
> computer system.
> >
> >
> > -----Original Message-----
> > From: DesignerCouncil [mailto:[log in to unmask]] On Behalf Of
> Jack Olson
> > Sent: Friday, June 20, 2014 11:55 AM
> > To: [log in to unmask]
> > Subject: Re: [DC] z-axis separation for high voltage
> >
> > Thanks for taking the time to respond (and to everyone else who responded
> > too),
> > and I understand your point about derating,
> > but I am more focused on the STARTING clearance for 1700V,
> >
> > IPC Table 6-1 gives me something slightly over 125 mils,
> > and my board is only 62 mil thickness, about half!
> > I wasn't initially worried
> > because if you look at the slash sheets for dielectric material, its more
> > in the KV range PER MIL
> > but now I'm starting to wonder...
> >
> > Where can I learn more about this?
> >
> >
> > On Fri, Jun 20, 2014 at 10:45 AM, Joel S. Peiffer <[log in to unmask]>
> wrote:
> >
> > > William provides some good advice to derate the materials insulation
> > > resistance significantly as well as providing some of the reasons for
> > > doing this (copper surface roughness, dielectric defects).
> > >
> > > I would like to go into a little more detail on derating.  The boards
> > > operating conditions (temp, humidity) and expected service life need
> to be
> > > taken into account as well.  High temp/humidity operating environments
> may
> > > call for additional derating.  The overlap area of high voltage should
> > > also be taken into consideration.  If the area is very small, the
> > > likelihood of a material defect is very small.  However, if the area is
> > > very large, the likelihood of a material defect will increase in
> > > proportion to the area and the material may have to be derated
> > > appropriately.  Finally, the derating should be dependent on the
> > > dielectric thickness.  Thus, thicker materials need to be derated less
> > > than thinner materials.  For example, a 0.5 mil defect may not have
> much
> > > impact on a 5 mil thick material but it will have severe consequences
> on a
> > > 1 mil thick material.
> > >
> > > If you need to utilize very thin dielectrics to ensure you meet you z
> axis
> > > thickness requirements, you may want to look at materials other than
> FR-4
> > > to provide the required insulation resistance requirements.  Some of
> the
> > > polyimide film materials have excellent insulation resistance and may
> be a
> > > better choice in this situation.
> > >
> > > Regards, Joel
> > >
> > >
> > > Joel S. Peiffer
> > > 3M Electronic Materials Solutions Division
> > > 3M Center, Building 201-1E-17
> > > St. Paul, MN  55144
> > > Tel:  (651) 575-1464
> > > Cell:  (612) 327-1983
> > > [log in to unmask]
> > >
> > >
> > >
> > > From:   "Brooks, William" <[log in to unmask]>
> > > To:     <[log in to unmask]>
> > > Date:   06/20/2014 10:11 AM
> > > Subject:        Re: [DC] z-axis separation for high voltage
> > > Sent by:        DesignerCouncil <[log in to unmask]>
> > >
> > >
> > >
> > > The epoxy/glass dielectric actually is spec'd at 750V per mil
> insulation
> > > resistance perpendicular to the layers according to Mil-P-13949/4C for
> FR4
> > > glass epoxy laminated materials.  So 1.3 mils minimum of material
> > > perpendicular to the layers would net you 1KV insulation resistance
> top to
> > > bottom or internal layer to layer.
> > >
> > > Always give yourself some margin... The back side of the copper foil is
> > > rough and can be 'spiked' on the laminated side for foil adhesion...
> those
> > > spikes can cause the spacing to be less than the minimum target spacing
> > > you require when laminated. Also there can be bubbles or voids in the
> > > materials that could occur right between your two high voltage
> > > conductors... Unless you are trying to mimic a capacitance plane pair,
> > > there is little or no reason to have the high voltage lines that close.
> > > You don't want a short to occur internally in the board. Give yourself
> a
> > > buffer of at least a couple of additional layers of 2 mil prepreg on
> > > internal layers. Just saying... :) Good design practice is to de-rate
> by
> > > 50%.
> > >
> > > I don't warranty sharing my observations... or advice... but if you
> feel
> > > the need to compensate me... I like microbrewery beers... the Darker
> > > Belgian style... I'm not a big hops lover... though I like the hoppy
> beers
> > > too just not as much...  :)
> > >
> > >
> > > William Brooks, CID+
> > > Senior MTS (Contract)
> > > 2747 Loker Ave West
> > > Carlsbad, CA 92010-6603
> > > 760-930-7212
> > > Fax:        760.918.8332
> > > Mobile:    760.216.0170
> > > E-mail:    [log in to unmask]
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: DesignerCouncil [mailto:[log in to unmask]] On Behalf Of
> Jack
> > > Olson
> > > Sent: Friday, June 20, 2014 7:35 AM
> > > To: [log in to unmask]
> > > Subject: [DC] z-axis separation for high voltage
> > >
> > > maybe I'm having a "not enough coffee yet" morning, but I was asked how
> > > much separation I need between layers for high voltage.
> > >
> > > We have a design that may have 1700V in several places.
> > > Since we are looking at a clearance into the board, layer-to-layer I'm
> > > pretty sure I can use the "internal" column B1 of Table 6-1 in IPC-2221
> > > (using Table 6-1 for z-axis was discussed in a committee meeting and no
> > > one
> > > disagreed)
> > >
> > > but the number I get for 1700V is =
> > > (.25 mm for the first 500V) plus (.0025 mm for each of the other
> 1200V, 3
> > > mm)
> > > equals 3.25 mm
> > >
> > > For one thing, it already seems like I'm off-track because .25 for 500V
> > > doesn't correspond very well with 3 mm for 1200V, but if you can't
> trust
> > > IPC..... well, let's not go there.
> > >
> > > My REAL question is that, although I'm safe using 3.25 mm, my board is
> not
> > > that thick!
> > > Is there a smaller z-axis clearance that can be used for 1700V? across
> > > typical FR4 material?
> > > (we are using a RoHS compatible 170Tg /126)
> > >
> > > What's the MINIMUM layer spacing I can use for 1700V?
> > >
> > > thanks,
> > > Jack
> > >
> > >
> > > ______________________________________________________________________
> > > This email has been scanned by the Symantec Email Security.cloud
> service.
> > > For more information please contact helpdesk at x2960 or
> [log in to unmask]
> > > ______________________________________________________________________
> > >
> > >
> > >
> ---------------------------------------------------------------------------------
> > > DesignerCouncil Mail List provided as a free service by IPC using
> LISTSERV
> > > 16.0.
> > > To unsubscribe, send a message to [log in to unmask] with following
> text in
> > > the BODY (NOT the subject field): SIGNOFF DesignerCouncil.
> > > To temporarily stop/(restart) delivery of DesignerCouncil send: SET
> > > DesignerCouncil NOMAIL/(MAIL) For additional information, or contact
> Keach
> > > Sasamori at [log in to unmask] or 847-615-7100 ext.2815
> > >
> > >
> ---------------------------------------------------------------------------------
> > >
> > >
> > >
> _____________________________________________________________________________
> > > Scanned by IBM Email Security Management Services powered by
> MessageLabs.
> > > For more information please visit http://www.ers.ibm.com
> > >
> > > This email is intended only for the use of the party to which it is
> > > addressed and may contain information that is privileged,
> confidential, or
> > > protected by law.  If you are not the intended recipient you are hereby
> > > notified that any dissemination, copying or distribution of the email
> or
> > > its contents is strictly prohibited.  If you have received this
> message in
> > > error, please notify us immediately, by replying to the message and
> > > deleting it from your computer.
> > >
> > > WARNING: Internet communications are not assured to be secure or clear
> of
> > > inaccuracies as information could be intercepted, corrupted, lost,
> > > destroyed, arrive late or incomplete, or contain viruses.  Therefore,
> we
> > > do not accept responsibility for any errors or omissions that are
> present
> > > in this email, or any attachment, that have arisen as a result of
> e-mail
> > > transmission.
> > >
> > >
> _____________________________________________________________________________
> > >
> > > ______________________________________________________________________
> > > This email has been scanned by the Symantec Email Security.cloud
> service.
> > > For more information please contact helpdesk at x2960 or
> [log in to unmask]
> > > ______________________________________________________________________
> > >
> > >
> > >
> > >
> ---------------------------------------------------------------------------------
> > > DesignerCouncil Mail List provided as a free service by IPC using
> LISTSERV
> > > 16.0.
> > > To unsubscribe, send a message to [log in to unmask] with following
> text in
> > > the BODY (NOT the subject field): SIGNOFF DesignerCouncil.
> > > To temporarily stop/(restart) delivery of DesignerCouncil send: SET
> > > DesignerCouncil NOMAIL/(MAIL)
> > > For additional information, or contact Keach Sasamori at
> [log in to unmask] or
> > > 847-615-7100 ext.2815
> > >
> > >
> ---------------------------------------------------------------------------------
> > >
> > >
> > >
> > > ______________________________________________________________________
> > > This email has been scanned by the Symantec Email Security.cloud
> service.
> > > For more information please contact helpdesk at x2960 or
> [log in to unmask]
> > > ______________________________________________________________________
> > >
> > >
> > >
> ---------------------------------------------------------------------------------
> > > DesignerCouncil Mail List provided as a free service by IPC using
> LISTSERV
> > > 16.0.
> > > To unsubscribe, send a message to [log in to unmask] with following
> text in
> > > the BODY (NOT the subject field): SIGNOFF DesignerCouncil.
> > > To temporarily stop/(restart) delivery of DesignerCouncil send: SET
> > > DesignerCouncil NOMAIL/(MAIL)
> > > For additional information, or contact Keach Sasamori at
> [log in to unmask]
> > > or 847-615-7100 ext.2815
> > >
> > >
> ---------------------------------------------------------------------------------
> > >
> >
> >
> > ______________________________________________________________________
> > This email has been scanned by the Symantec Email Security.cloud service.
> > For more information please contact helpdesk at x2960 or
> [log in to unmask]
> > ______________________________________________________________________
> >
> >
> ---------------------------------------------------------------------------------
> > DesignerCouncil Mail List provided as a free service by IPC using
> LISTSERV 16.0.
> > To unsubscribe, send a message to [log in to unmask] with following text
> in
> > the BODY (NOT the subject field): SIGNOFF DesignerCouncil.
> > To temporarily stop/(restart) delivery of DesignerCouncil send: SET
> DesignerCouncil NOMAIL/(MAIL)
> > For additional information, or contact Keach Sasamori at [log in to unmask]
> or 847-615-7100 ext.2815
> >
> ---------------------------------------------------------------------------------
> >
> > ______________________________________________________________________
> > This email has been scanned by the Symantec Email Security.cloud service.
> > For more information please contact helpdesk at x2960 or
> [log in to unmask]
> > ______________________________________________________________________
> >
> >
> >
> ---------------------------------------------------------------------------------
> > DesignerCouncil Mail List provided as a free service by IPC using
> LISTSERV 16.0.
> > To unsubscribe, send a message to [log in to unmask] with following text
> in
> > the BODY (NOT the subject field): SIGNOFF DesignerCouncil.
> > To temporarily stop/(restart) delivery of DesignerCouncil send: SET
> DesignerCouncil NOMAIL/(MAIL)
> > For additional information, or contact Keach Sasamori at [log in to unmask]
> or 847-615-7100 ext.2815
> >
> ---------------------------------------------------------------------------------
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please contact helpdesk at x2960 or [log in to unmask]
> ______________________________________________________________________
>
>
> ---------------------------------------------------------------------------------
> DesignerCouncil Mail List provided as a free service by IPC using LISTSERV
> 16.0.
> To unsubscribe, send a message to [log in to unmask] with following text in
> the BODY (NOT the subject field): SIGNOFF DesignerCouncil.
> To temporarily stop/(restart) delivery of DesignerCouncil send: SET
> DesignerCouncil NOMAIL/(MAIL)
> For additional information, or contact Keach Sasamori at [log in to unmask]
> or 847-615-7100 ext.2815
>
> ---------------------------------------------------------------------------------
>


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please contact helpdesk at x2960 or [log in to unmask] 
______________________________________________________________________

---------------------------------------------------------------------------------
DesignerCouncil Mail List provided as a free service by IPC using LISTSERV 16.0.
To unsubscribe, send a message to [log in to unmask] with following text in
the BODY (NOT the subject field): SIGNOFF DesignerCouncil.
To temporarily stop/(restart) delivery of DesignerCouncil send: SET DesignerCouncil NOMAIL/(MAIL)
For additional information, or contact Keach Sasamori at [log in to unmask] or 847-615-7100 ext.2815
---------------------------------------------------------------------------------

ATOM RSS1 RSS2