Hi again Paul,
 
One last note.
 
In my wording notice that I used the word "non-conformance", not defect, reject, scrap, junk, etc....
 
The next step is MRB, where the real decisions/action get made in light of the facts, and in conjunction with customer involvement.
 
Gerry

 
> Date: Fri, 6 Dec 2013 08:32:37 -0500
> From: [log in to unmask]
> Subject: Re: [TN] Crazing
> To: [log in to unmask]
> 
> Hi Gerry,
> 
> Bill and I are doing well.
> 
> I concur with your thoughts. If you find something using a method that
> is not required for the defect, it's still a defect. 
> 
> I am not happy with the idea that because I found the crazing during a
> microscopic examination it does not count.
> 
> 
> Sincerely,  
> 
>  
> 
> Paul Reid 
> 
> Program Coordinator  
> 
> PWB Interconnect Solutions Inc. 
> 235 Stafford Rd., West, Unit 103 
> Nepean, Ontario Canada, K2H 9C1 
> 
> 613 596 4244 ext. 229  
> 
> Skype paul_reid_pwb 
> [log in to unmask] 
> 
>  
> 
> 
> -----Original Message-----
> From: TechNet [mailto:[log in to unmask]] On Behalf Of Gerry Gagnon
> Sent: December 6, 2013 8:21 AM
> To: [log in to unmask]
> Subject: Re: [TN] Crazing
> 
> Hi Paul,
>  
> Hope you and Bill B. are doing fine.
>  
> I am assuming that you you were looking for something else and detected
> a "non-conforming" level of crazing.
>  
> In my mind, this is an easy one because you found the non-conformance
> "along the way" while examining your microsection.
>  
> Let me give you an easier analogy.
>  
> While examining a region of an IST test coupon in transverse mount, I
> find a tiny piece of material bridging two conductors at high mag.
> Clearing away  the conductor surfaces enough to measure if there is a
> resistance, I get a value in the MegOhm range.
>  
> Is it a short?
>  
> Unless things gave changed, Bare board continuity thresholds will not
> detect this phenomenon.
> Let's also say that innerlayer AOI (if performed) has a very high escape
> rate for this type of phenomenon or may not even detect it at all.
>  
> Is the phenomonon a short per IPC A-610?
> My answer is yes, it is an unwanted connection, albeit a high resistance
> connection, and is difficult to detect. 
>  
> Does the fact that I found this short in a cross section under high
> magnification, while I was looking for something else, change anything?
>  
> I don't think so, and I do not think IPC A-610 allows non-conformances
> that are found "along the way". 
>  
> Have a good one.
> Gerry
>  
>  
> 
>  
> > Date: Thu, 5 Dec 2013 16:05:41 -0500
> > From: [log in to unmask]
> > Subject: [TN] Crazing
> > To: [log in to unmask]
> > 
> > I was just on a conference call where we found crazing (a separation
> > between glass fibers and the epoxy system), in a microsection. The
> > fabricator stated that this had to be evaluated looking at a board
> > macroscopically and could not be evaluated microscopically. 
> > 
> >  
> > 
> > Crazing is called out in IPC-A- 600 in section 2, paragraph 2.3.2 page
> > 18, which is "Externally Observable Characteristics". In A-600 there
> is
> > picture of a microsection showing the defect but it states that a
> > microsection is not required.
> > 
> >  
> > 
> > In IPC 6012-2010 crazing is call out in 3.3.2.2, page 12, which states
> > (I am paraphrasing), "Crazing shall not violate greater than 50% of
> the
> > distance between adjacent conductors..." The document then refers to
> IPC
> > A 600.
> > 
> >  
> > 
> > What is your take on their argument that crazing should not be
> evaluated
> > microscopically as per IPC?  
> > 
> >  
> > 
> > Sincerely, 
> > 
> >  
> > 
> > Paul Reid 
> > 
> > Program Coordinator 
> > 
> > PWB Interconnect Solutions Inc. 
> > 235 Stafford Rd., West, Unit 103 
> > Nepean, Ontario Canada, K2H 9C1 
> > 
> > 613 596 4244 ext. 229  
> > 
> > Skype paul_reid_pwb 
> > [log in to unmask] 
> > 
> >  
> > 
> > 
> > ______________________________________________________________________
> > This email has been scanned by the Symantec Email Security.cloud
> service.
> > For more information please contact helpdesk at x2960 or
> [log in to unmask] 
> > ______________________________________________________________________
>  		 	   		  
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud
> service.
> For more information please contact helpdesk at x2960 or
> [log in to unmask] 
> ______________________________________________________________________
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please contact helpdesk at x2960 or [log in to unmask] 
> ______________________________________________________________________
 		 	   		  

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please contact helpdesk at x2960 or [log in to unmask] 
______________________________________________________________________

ATOM RSS1 RSS2